Pop,
If u run dual heaters (without running a separate line) does it throw a breaker or what?
|
|
|
12-21-2011, 04:20 PM
|
#12
|
Guest
|
Done more than enough sub zero camping in the TM. Can’t say it was fun but it was do-able. Before I can try to answer your question it would help to know if you will have hookups or if you are boon docking and if you have a generator also, how long will you be camping.
Ed
|
|
|
12-21-2011, 04:47 PM
|
#13
|
TrailManor Master
Join Date: Oct 2010
Location: Fayetteville, NC
Posts: 621
|
On our last trip we ran the heat strip in the Ac unit and an additional heater we got from Sams Club. Worked ok for about 5 minutes then it tripped the main 30A ac breaker in the TM. The additional heater had a low setting so we tried again with it on low and it no longer tripped the breaker. In the future, if we need the high setting I will run another heave duty cord to the 20A plug on the CG pedestal for the extra heater.
__________________
Previous owners of a great 2010 [SIGPIC][/SIGPIC] TM2720SL.
|
|
|
12-21-2011, 06:33 PM
|
#14
|
TrailManor Master
Join Date: Oct 2011
Location: New Braunfels, Texas
Posts: 919
|
We are in Sedona this week with temps in the low 30's. We are using the furnace a few times during the night and a ceramic electric heater placed on the floor. I'm turning off the camp water hose at night. I'm also running the water heater on electric mode. I've got an antifreeze in the gray tank. We don't expect temps dropping in the 20's or teens.
__________________
rvcycleguy
TM-2002 3124KB
TV-2003 Toyota Tundra V8 4.7L. Fact. Tow Pkg, air bags
2006 Suzuki Boulevard C50c Motorcycle- crashed- parted out
1956 Royal Enfield Bullet 500 Motorcycle-sold
2006 Harley Road King
|
|
|
12-23-2011, 03:14 PM
|
#15
|
Guest
|
Quote:
Originally Posted by moaboy
Pop,
If u run dual heaters (without running a separate line) does it throw a breaker or what?
|
Someone else might correct my simplified math, but ...
A 1500 watt appliance will draw approximately 15 amps at 120 volts. Two will draw 30 amps.
The TM plugs into a 30 amp receptacle. Just the two heaters puts you right at capacity.
Theoretically, if you ran only the two heaters, meaning no lights, no fans, no heater, no charging the batteries, no flushing the toilet, then you might squeak by.
|
|
|
12-23-2011, 05:27 PM
|
#16
|
TrailManor Master
Join Date: Aug 2010
Location: Orange County, California
Posts: 432
|
Quote:
Originally Posted by PopBeavers
Someone else might correct my simplified math, but ...
A 1500 watt appliance will draw approximately 15 amps at 120 volts. Two will draw 30 amps.
The TM plugs into a 30 amp receptacle. Just the two heaters puts you right at capacity.
Theoretically, if you ran only the two heaters, meaning no lights, no fans, no heater, no charging the batteries, no flushing the toilet, then you might squeak by.
|
Well, I cannot disagree with the math. However, I ran two 1500 watt electric heaters last January in Tucson and then a few times during the night the TM heater kicked on. That is more than 3000 watts, but the breakers did not kick off.
Tom
__________________
TM 3023
TV 2010 F-150 4.6, factory tow pkg, air bags
|
|
|
12-23-2011, 07:01 PM
|
#17
|
Site Team
Join Date: Feb 2003
Location: The mountains of Scottsdale, AZ, and the beaches of Maine
Posts: 10,200
|
Well, PopBeavers has done the quick approximate math (my favorite approach to problems) quite correctly. He concludes that two 1500-watt heaters are just about at the limit of total current. If you want to be more precise, you need to say "1500 watts at 120 VAC = 12.5 amps, so two heaters is 25 amps, leaving 5 amps to spare". But this much precision isn't really warranted, because so many other things are approximate. The voltage is probably lower than 120 volts, so the each heater draws a bit less than 12.5 amps. The manufacturer of the heaters leaves some slack in his build - he doesn't want the hassle of having his heaters pop breakers in someone's home. And by design, the 30-amp breaker will hold at 30 amps forever, and at 31 amps, or 32 amps, for a long time. So Pop's initial conclusion is correct - two 1500-watt heaters will work, but you can't add too much more without popping the 30-amp breaker.
In this case, working harder doesn't really produce a better result. The "approximate" approach is fine.
Bill
|
|
|
12-23-2011, 08:24 PM
|
#18
|
Guest
|
So looks like I could run my two ceramic heaters on low which would total 2000 watts and have some juice (amps) left over?
|
|
|
12-23-2011, 09:32 PM
|
#19
|
Guest
|
One of the major heat loss places is from under the pull-out bed. It is pretty easy to heat the top of the bed (more clothes, blankets, heaters, etc.) but much more difficult to insulate the bottom. I think I would be inclined to add a 1" or so thick piece of closed-cell foam under the mattress to add insulation if I spent more time camping in cold climates.
|
|
|
12-23-2011, 09:59 PM
|
#20
|
TrailManor Master
Join Date: Feb 2008
Location: D.C. Metro Area
Posts: 290
|
You might want to reference this post and how I've used a 1500w heater and two 200w heaters to keep everything warm and toasty: http://www.trailmanorowners.com/foru...highlight=200w
Also remember that you'll need to wipe down all the windows in the morning from all the condensation in very cold weather.
__________________
2002 Tahoe 'Marge'
2015 Silverado
2006 2720SL 'Homer'
Prodigy Brake Controller
2.5" Factory Lift Kit
15" Dexstar Wheels
15" Karrier Loadstar Tires w/TR-416 Stems
Bill's Screen Door kit
And a host of other mods...
14 y.o. 'Sasha' (aka 'Miss Kitty), started fostering 12/24/10 and adopted 3/15/11
[SIGPIC][/SIGPIC]
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|